j_erickson said:
Not if you are not touching the service
I'm sorry, I don't see where the exception applies. 250.50 is a short paragraph. Could you quote the paragraph where adding elements to a GES are exempt if you're not upgrading the service? If he's putting on an addition, the Code requires new work to comply with the current Code. The Code isn't making him go back and tie in the old work. Of course, the old work doesn't have to be changed, unless you are modifying the old work. The CEE is a non-issue in old work, and the Code writers understand that. The 2005 code language in 250.50 was specifically changed to explain that if it's there it must be used. The clarification was intended for the benefit of the AHJ. IAEI wrote a pretty good article on the matter in the October 2005 on-line magazine.
1424 cdt - The requirement has nothing to do with the service. It has everything to do with the building or structure being serviced, and the establishment of an effective grounding electrode system.
Let's say he drives a 5/8" copper rod 10' into the earth next to the addition. Would he have to tie it into the GES if it's there? Yes, he would. But assuming he has not driven the rod and has met the minimum requirements of 250.52, he wouldn't have to drive a rod. One could argue successfully that the rod doesn't have to be bonded if not present. Yep, that's a fact. Pull the rod out and you don't need to bond it.
Likewise, if there is no CEE, the Code does not require its installation. The Code is also specific that the CEE is in a foundation or footing in direct contact with the earth, meaning no vapor barrier, exempli gratis. There is no mention of CEE in concrete flooring. Now, if the folks putting in the footings and/or foundation elect to use reinforcing rods of #4 or larger, with 20 or more feet of total rod length, they're in there and you must use them in your GES. If they choose not to use rebar for some reason, and local building codes don't require them, you're off the hook. No CEE, no bond.
[edited 1403 cdt] If the CEE is not not copper, it must be no less than 1/2" in diameter. If it is copper, it is permitted to be not smaller than 4AWG. Any GEC not meeting this diameter requirement does not meet the requirement of 250.52(a)(3) and is not required to be connected to the GES. So, 3/8" (#3) or smaller rebar wouldn't be required to be bonded to the GES.
Dan