Cavie said:
Tbonse, This is where you are missing the point. The code does not say that the rebar must be bonded. The code says that the rebar must be used as a cee "IF" you are building a service.
I was at a Halloween party last night. I just got up. The coffee pot is spewing. First, Cavie, quote me the part where "building a service" comes into play.
Now, everybody get out your books and turn to 250.52(A)(3).
Note that there is no black bar running vertically on the left side of that paragraph. That indicates the paragraph has not changed at all since the 2002 code. So, we've had 4 years, at least, to learn that a CEE is:
1. Located within and near the bottom of a concrete foundation or footing
2. The concrete in (1) is in direct contact with the earth
3. The length of the electrode is 20 ft or longer
4. It's made of some form of coated conductive steel at least 1/2" in diameter, OR it's made of bare copper of at least #4 AWG
Not in floor, not in wall. Foundation or footing, no vapor barrier, no insulation.
Ready?
Turn to 250.50. It's one page back. Notice the black bar running down the left side of the paragraph - ALL of it. That means the ENTIRE paragraph was rewritten in the 2005 Code. So, we all have the excuse that *this* is only 1.824 years old, as of today, so we haven't had time to get our heads around it. (Somebody had better check my math on that - first pull off the coffee.)
The paragraph is two sentences long. It is a long sentence pair, and linguisticians would say it's too long for the average population. They may be right.
I'll deal with the long single-sentence exception later. First, let's break down the first sentence.
A.
"All grounding electrodes as described in 250.53(A)(1) through (A)(6)..."
The CEE I defined at the beginning of this posting is 250.53(A)(3). That is between (1) and (6), so it applies.
B.
"... that are present at each building or structure..."
This means that if the building or structure in question contains the thingy in 250.52(A)(3)
C.
" ... served ..."
This means the building or structure either has electrical service or will have it shortly.
D.
"... shall be bonded together to form a grounding electrode system."
Seems clear enough. What about the second sentence? Maybe that's the problem.
E.
" Where none of these grounding electrodes exist, ..."
Remember we're talking about the thingies in 250.52(A)(1) through (6).
F.
"... one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(7) shall be used."
I thought about breaking this one in two, to emphasize "one or more", but let's press on. The concrete-encased electrode is 250.52(A)(3). So, if it doesn't EXIST, you don't have to make one. This is because the second sentence only requires one or more of (A)(4) through (A)(7), which *doesn't* include (A)(3).
The exception must be the problem. So far, all is clear.
"Exception: Concrete-encased electrodes..."
Jackpot! The exception is CEE's! Whoopee!
" ... of existing buildings or structures..."
You see, the building or structure is already here, so I'm exempt!
"... shall not be required to be part of the grounding electrode system..."
That's it. Am I still typing? Let it go, for God's sake.
"where the steel reinforcing rods are not accessible for use..."
If I cover them up fast enough, they won't be accessible.
"without disturbing the concrete."
OK. Now, if you intentionally disturb the concrete and expose the CEE as painfully and protractedly defined in this and earlier posts, guess what? The execption *doesn't* apply. I also submit that in new construction (which includes modifying old construction, ladies and gentlemen) if the trades don't play well together, and cement head covers up the CEE before Sparky gets there, *someone* has dropped the ball, probably the GC. The other possibility is a "screw the other trades" attitude, which besides being unprofessional leads to a Code violation in this instance.
If you build a utility shed and put #5 rebar in the footings, and you have more than 20 feet of rebar, essentially meeting the definition of 250.52(A)(3), but you never plan to electrify the utility shed, knock yourself out. There is no requirement to do anything in that instance. You don't need to do a thing.
If you come back 10 years later and put an outlet in for lighting, you *still* don't have to use the CEE, by exeption, because you'd have to ding up (sic) the existing concrete to get to it.
If you're building a new building or structure now and plan to electrify it, *and* CEE meeting the requirements of 250.52(A)(3) exists, YOU MUST USE IT and see to it that bonding means are made prior to encasing the electrode with concrete. Period.
"Ignorance of the law is no excuse." - Unknown
"I'm tryin' to think but nothin' happens." - Curly Howard
Dan