iwire said:Here in MA if it is a new footing that has rebar in it you must use it.
If the GC went ahead and allowed the pour without getting an EC to make GEC connection and have it inspected the GC will have to break some concrete.
That makes sense, since with the proper coordination, the electrode would have been available without having to break concrete.
It seems like the general contractor tends to call the electricians after the foundation is already poured. For fellow engineers, I think its a good idea to try to get a note about the CCE on the structural drawings.