DonaldKMorgan
Member
250.52(A)(3)describes what a CEE is and the requirements for it, but I am concerned about the effects of the concrete on the bare copper. We have always been told to protect the bare copper from concrete to allow the copper to remain intact. Exhibit 250.22 shows a sleeve as the copper emerges from the slab but the connection is still in the concrete. One answer was to turn the rebar up into an interior wall and make the connection there, however our inspector insists that the connection be accessible. 250.68 (A) Exception No. 1 could apply but, I think the writers were referring to the connection that is actually encased. Finally my interpertation to the requirement for CEE was to enhance the current grounding requirements not to replace them, am I incorrect in this thnking?