I'm with Mr. Carroll, except we ask for the 20' of copper in the footing on all new jobs. We do a lot of post tension slabs here.
What is the reply when you ask for this?
I'm with Mr. Carroll, except we ask for the 20' of copper in the footing on all new jobs. We do a lot of post tension slabs here.
Let me spin this a bit further;
For the areas that do not require utilizing the CEE for a building addition would a new metal water line (that qualifies as a grounding electrode) added to the same addition be ignored also and not made part of the GES?
Pete
If it's an addition w/o service upgrade or change, we don't require the connection in my town.
What is the reply when you ask for this?
I say yes it should be used and would require a supplemental 250.53(D)(2).
Now I will spin it further.
You have an existing metal waterline properly installed and add a metal waterline to an out building (assuming 10'). 250.50 requires ALL electrodes present.
How do you isolate it so as not to have objectionable current running on the interior lines to this new electrode.
If you require it to be isolated what code would you cite?
This would also be a bonding jumper, correct?
I say yes it should be used and would require a supplemental 250.53(D)(2).
Now I will spin it further.
You have an existing metal waterline properly installed and add a metal waterline to an out building (assuming 10'). 250.50 requires ALL electrodes present.
How do you isolate it so as not to have objectionable current running on the interior lines to this new electrode.
If you require it to be isolated what code would you cite?
This would also be a bonding jumper, correct?
It's actually in our ordinance and a lot of jurisdictions ask for it here so it's pretty common practice. Just to be clear, we don't get it on addidtions unless they are moving the service to the addition, but it is required on all new buildings.
I agree. An addition with 20' of 1/2" or larger rebar in the footing would not be required to be used if the service is not touched. The service was code compliant when it was installed and can remain as is.
What if the house had a well and as part of the new addition project the well was abandoned and a new copper water line was run into the house from the street?![]()