I am not saying remove it. I am saying not to install it.
250.50 Grounding Electrode System. All grounding electrodes
as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bonded
together to form the grounding electrode system.
It is present. Separating it from the earth does not make it disappear.
"Where the words "?if available?" were used in previous editions of the Code in this section, they were to mean where there is an electrode that meets the criteria of any of the grounding electrodes specified in Section 250.52(A) (1) through (6), then it should be used in the grounding electrode system.
Let?s face it, "if available? was not the best language to use in a
mandatory requirement of the Code."
From:
http://www.iaei.org/blogpost/890108...odes-Required?hhSearchTerms="concrete"&terms=