Concrete Tight Fittings For EMT

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Never had to use these for EMT. How are they different? I imagine they are more expensive. I tried to look on Bridgeports site but did not find.
 
Yep, but it can be tricky since the code says approved and not listed.

My experience is that most inspectors accept this, but a few have qualms.
Yes, and most don't comply with the listing requirement. The following is from the UL Guide Information for "Conduit Fittings (DWTT).
A fitting that is taped completely (from the raceway to the box, or raceway to raceway) is concrete-tight when the product carton is marked "CONCRETE-TIGHT WHEN TAPED."
However if you do that the inspector/AHJ should accept it as it part of the listing.
 