Condensate pump

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have condensate pump direct wire which is less than 1/8 HP. I looked at NEC 2014 422.31(A)says local disconnect not require but not sure if I have the correct code section. Should it have local disconnect?
 
No local disconnect needed IF you meet the 422.31A requirements:::

where the switch or circuit breaker is within sight from the
appliance or is lockable in accordance with 110.25.
 
2014 NEC:
422.31 Disconnection of Permanently Connected Appliances.
(A) Rated at Not over 300 Volt-Amperes or 1 ⁄ 8 Horse-power. For permanently connected appliances rated at not over 300 volt-amperes or 1 ⁄ 8 hp, the branch-circuit overcurrent device shall be permitted to serve as the disconnecting means.

2017 NEC:
422.31 Disconnection of Permanently Connected Appliances.
(A) Rated at Not over 300 Volt-Amperes or 1 ∕ 8 Horsepower. For permanently connected appliances rated at not over= 300 volt-amperes or 1 ∕ 8 hp, the branch-circuit overcurrent device shall be permitted to serve as the disconnecting means where the switch or circuit breaker is within sight from the appliance or is lockable in accordance with 110.25.
 