- Illinois
- retired electrician
Re: condo design
hardworkingstiff ,
There is only a very small change in the efficiency of a resistance heating device when the voltage changes from 240 to 208. The only change in efficiency is the very small additional heat losses to the ambient air as a result of the longer time it will take for the element to heat the water to the desired temperature.
Lets look at some numbers. First we have to remember that for all practical purposes there will be no difference in the resistance of the heating element when the voltage is changed from 240 to 208. If you take a water heater element with a 3000 watt rating at 240 we find the resistance is 19.2 ohms. If we supply this same element with 208 volts we will have heating equal to 2253 watts. Water weighs about 8.3 pounds per gallon so a 40 gallon water heater would have 332 pounds of water. One BTU or 0.293 watthours are required to raise one pound of water 1?F. If the water supply is 50?F and the desired temperature is 120?F, then we need 6809 watt-hours to heat this water. With a 240 volt supply this will take 2.27 hours and with the 208 volt supply it will take 3.02 hours, but the total energy used remains the same.
Don
hardworkingstiff ,
Don