I have inherited a 6 unit condo,each unit seperated by 2 hr fire wall that extends to the roof line. They were running 3-wire feeders from a 6 gang meter center mounted on the building. They have copper waterlines coming from the street to each unit. They were catching the pipes from the remote panels. I put the brakes on the job because I told them they were single family dwellings and the meter center could not be mounted on the building , the feeders could not be run in the attics and the water lines must go to the meter center(suggested setting pedistal and running UG feeders to each unit w/ disc at each and rod) then they could catch that panel. They then produced paperwork saying the outside and attic were common area owned by the HO asso. I accepted the letter(reluctantly)but required 4-feeders of coarse and require the WP ground to be taken to each unit to the 6 gang center. I did tell him he could daisy chain all the waterlines together if he wanted.The EC is raising cain and does'nt think its right. Any thoughts?? Where are u Ryan, I need you brother.