Condo grounding
necbuff
I have inherited a 6 unit condo,each unit seperated by 2 hr fire wall that extends to the roof line. They were running 3-wire feeders from a 6 gang meter center mounted on the building. They have copper waterlines coming from the street to each unit. They were catching the pipes from the remote panels. I put the brakes on the job because I told them they were single family dwellings and the meter center could not be mounted on the building , the feeders could not be run in the attics and the water lines must go to the meter center(suggested setting pedistal and running UG feeders to each unit w/ disc at each and rod) then they could catch that panel. They then produced paperwork saying the outside and attic were common area owned by the HO asso. I accepted the letter(reluctantly)but required 4-feeders of coarse and require the WP ground to be taken to each unit to the 6 gang center. I did tell him he could daisy chain all the waterlines together if he wanted.The EC is raising cain and does'nt think its right. Any thoughts?? Where are u Ryan, I need you brother.
Re: Condo grounding
Are there circuit breakers in the meter center? Why don?t you want the meter center mounted on the building?
Re: Condo grounding
There are breakers in the meter center. The reason I did'nt want it on the building was most of the time that type of set up is treated as separate structures due to property lines and 2 hr firewalls. You can't put equipment or run feeders on or thru someone elses property. They made the situation fit they're needs by getting me a letter of "common area".I don't have much of a problem there, it's the EC arguing about the grounding cost. All those waterlines must go back to the service equipment. Possible exception: If being treated as multiple occupancy, and they run PVC into each unit, they could come out of the sub-panel to bond the pipes. But I do not think the city will permit non-metallic lines to a structure. Thats the only alternitative I see and thats a stretch because I think they are actually single family's, paint to paint ownership. Not like an apt w/ no ownership.
Re: Condo grounding
I would have no problem with a single GEC to the street side of the closest water service tied to all of the service panels at the meter area and a bonding jumper from the EGC at each unit to the water piping in that unit.
Re: Condo grounding
I agree with Don.
Connect the closest underground water service, ground rod, ufer, etc to the meter stack.
From the meter stack run 4-wire cables to each units panel.
Bond each units water service to the equipment grounding buss in the panels.