Article 100 says a firewall makes a structure a building. So four townhouses separated by firewalls would be considered four "buildings." Common practice is to put a meter center with four breakers at one end and run SER feeders to each dwelling unit with firestopping at each firewall.
Does this comply with 225.30?
How about 225.31?
We tried to tell an owner to run the feeders under the slab to each dwelling unit, but he wants to do it with SER between the second floor joists.
Does this comply with 225.30?
225.30 Number of Supplies. A building or other structure that is served by a branch circuit or feeder on the load side of a service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit. Where a branch circuit or feeder originates in these additional buildings or other structures, only one feeder or branch circuit shall be permitted to supply power back to the original building or structure, unless permitted in 225.30(A) through (E).
How about 225.31?
225.31 Disconnecting Means. Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
We tried to tell an owner to run the feeders under the slab to each dwelling unit, but he wants to do it with SER between the second floor joists.