Are conductors considered accessible at conduit bodies?
Don
Don
In addition, Section 314.29 requires that they are also to be Accessible (as applied to wiring methods)enough to provide the access to the conductors.Conduit Body. A separate portion of a conduit or tubing system that provides access through a removable cover(s) to the interior of the system at a junction of two or more sections of the system or at a terminal point of the system.
Boxes such as FS and FD or larger cast or sheet metal boxes are not classified as conduit bodies.
I don't think so.Wires in concealed raceways are considered concealed, even though they may become accessible by withdrawing them.
DonAccessible (as applied to wiring methods). Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building.
Don, I think you answered your initial question with the definition of Accessible.200.6 Means of Identifying Grounded Conductors.
(B) Sizes Larger Than 6 AWG.An insulated grounded conductor larger than 6 AWG shall be identified either by a continuous white or gray outer finish or by three continuous white stripes on other than green insulation along its entire length or at the time of installation by a distinctive white marking at its terminations.
250.119 Identification of Equipment Grounding Conductors.
(A) Conductors Larger Than 6 AWG.An insulated or covered conductor larger than 6 AWG copper or aluminum shall be permitted, at the time of installation, to be permanently identified as an equipment grounding conductor at each end and at every point where the conductor is accessible.
90-4 in actionOriginally posted by rbalex:
Oddly enough, the local authority justified using only black, unidentified conductors as a safety measure.