Note: I have never used Neher - McGrath. I don't plan on using Neher - McGrath.
It is not a bad assumption. Sadly, it is not correct. The Neher McGrath method applies to underground installations, for which the physical properties of the dirt (and perhaps concrete encasement) come into play.
Okay, one more hint, then I need to leave this alone.
310.15.A.1, Tables or Engineering Supervision
310.15.C, Engineering supervision
The equation is not limited to underground.
Informative Annex B, Application Information for Ampacity Calculation
B.2 Typical Applications Covered by Tables
This cites the Neher - McGrath equation and references IEEE 835
Table B.310.15.B.2.1 is for conductors in raceway in free air, 30C ambient.
Table B.310.15.B.2.3 is for conductors in raceway in free air, 40C ambient.
IEEE 835 Std Power Cable Ampacity Tables
A.2.3 Example 3: 3-1/c 2000 kcmil copper, 15 kV, tape shielded, EPR cables installed in a 6 Inch PVC in still air.
Yes, this is a Neher - McGrath calculation
So, yes, N-M does apply in free air.
No, the Secret Squad formula is not derived from that. And I think Ethan already knew this.
Signed
A
(for anonymous)