I am trying to size the conductors for this spot welder. My understanding according to 630.31(A)(1) is that I take the rated VA (25,000), and divide by the rated primary voltage (220v) to get the rated primary current (114 Amps). Then, since it's a manually operated welder, I take 50% of 114 to get my conductor ampacity (57 Amps). Does that sound right? My understanding is that the duty cycle multipliers in Table 630.31(A) only apply if your welder is used with the exact same settings/load every time, which sounds like something that would be the case for an automated setup, not manual.