Conductor ampacity for overhead crane circuit.

steve61

licensed Electrical Contractor
Location
Nebraska
Occupation
Electrician
I have an overhead crane that I need to run a 460 volt 3 phase circuit to. After doing the amperage calculations and coming up with 46.375 amps ( # 8 thhn in the 75 degree column) I got an actual picture of the crane nameplate showing a required circuit ampacity of 115 amps. With the value of 115 amps, do I need to multiply 115 by 1.25 getting 143.75 amps needing # 1/0 wire or go just with the name plate rating of 115 amps and # 2 wire ? (all amperages from the 75 degree column).
 
crane nameplate showing a required circuit ampacity of 115 amps. With the value of 115 amps, do I need to multiply 115 by 1.25 getting 143.75 amps
I think you need to know how the nameplate required ampacity was calculated. The 125% may already be included like it is for the AC minimum circuit ampacity.
 
See 610.14. I don't think it is that simple.

The nameplate rating at 100% but the wire size might require you to have the duty rating.

Is this just the feeder circuit to a industrial control panel (409.20) or is this to the crane itself?
 
This is just the circuit to the crane itself. Name plate on the main control panel for the crane system.
 
I haven't dealt with Art 610 to be anywhere close to proficient but it certainly appears a #2would more than adequate.
 