So when derating due to having more than 3 CCC's in a raceway you can have up to 20 #10's and still good for 20 amps?
Correct.So that is 6 full boats and one circuit for a total of 19 circuits (assuming three phase) or 10 circuits with no MWBC's. Gunna need 1.25 pipe!
Yeah pretty much everything will have the -2 rating which means 90 wet or dry.Isn't all insulation rated for 90 degree nowadays?
Most probably is, but it would be worth checking if you just happen to be running in a wet location.Isn't all insulation rated for 90 degree nowadays?