NEC 310-15(B)(2)a requires derating of current carrying conductors according to the table. In case of raceway containing motor feeder conductors and control conductors (such as LOS, high temp sw, solenoid valves etc.,) I beleive that derating of the feeder cable is not required (unless it has mutiple pairs per phase etc.,)per exception contained for different systems (300-3). The control conductors are derived from a control power transformer (CPT with 120 V secondary) and would also qualify as Class 1 remote control and signalling circuit (less than 600V).
It stands to reason that there is really no threat to overheating of the phase cables within the raceway due to control cables (say #14) which in worst case can carry the maximum output of the CPT (typically 4 to 5 Amps) before the CPT fuse blows and thus removing all currents from the feeder cables to motor. The NEC is somewhat vague in this matter. The reason for derating is the heating effect of cables within a confined space such as a raceway - but control cables (Class 1) do not really contribute to the heating effect and should not be included in the derating calculations - Can anyone comment on this
Thanks
Mark Balan, PE.,
It stands to reason that there is really no threat to overheating of the phase cables within the raceway due to control cables (say #14) which in worst case can carry the maximum output of the CPT (typically 4 to 5 Amps) before the CPT fuse blows and thus removing all currents from the feeder cables to motor. The NEC is somewhat vague in this matter. The reason for derating is the heating effect of cables within a confined space such as a raceway - but control cables (Class 1) do not really contribute to the heating effect and should not be included in the derating calculations - Can anyone comment on this
Thanks
Mark Balan, PE.,