Conductor derating
dougbil
New member
Where is the Code does it allow me to use the 90 degree C column ampacity rating for derating a 90 degree C rated #2 XHHW cable for ambient temperature or more than three current carrying conductors in a raceway and not the 60 or 75 column based on the temperature limitations of the terminations?
try 110.14(C)
last sentance states
"Conductors with temperature rating higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both."