Conductor derating

Status
Not open for further replies.

dougbil

New member
Where is the Code does it allow me to use the 90 degree C column ampacity rating for derating a 90 degree C rated #2 XHHW cable for ambient temperature or more than three current carrying conductors in a raceway and not the 60 or 75 column based on the temperature limitations of the terminations?
 
Last edited:
try 110.14(C)
last sentance states

"Conductors with temperature rating higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both."
 