I could use some help to determine the conductor fill in a conduit seal ,
Article 501.15(C)(6)
my application has 24 # 12 THHN and 6 # 10 THHN
in table 5 I see approximate diameter and approximate area
do I use the diameter or area
I see the cross-sectional area must not exceed 25% the conduit
#12THHN =.130 x 24 conductors = 3.12
and
#10THHN =.164 x 6 conductors = .984
total 4.104
the next question do I use nominal or total area
a 3" conduit
if nominal is 3.085 and 25% is .7725
it must be area 7.457 and 25% is 1.86875
this is were need help
I have done this before I just can't remember the correct method
thanks