In article 501.20 states "where condensed vapors or liquids may collect on , or come in contact with , the insulation on conductors, such insulation shall be of a type identified for use under such conditions; or the insulation shall be protected by a sheath of lead or by other approved means."
I have installed a beldon 8761 to a veeder root system(fuel system) in a class 1 division 1 location. The cable is in conduit per hazardous locations but the beldon cable 8761 cable is not gas and oil resistance. Is there anything you can do without removing the cable? Does the cable have to be gas and oil resistance?
I have installed a beldon 8761 to a veeder root system(fuel system) in a class 1 division 1 location. The cable is in conduit per hazardous locations but the beldon cable 8761 cable is not gas and oil resistance. Is there anything you can do without removing the cable? Does the cable have to be gas and oil resistance?