Hey everyone. I am designing a PV system using a SolarEdge 17.3kus 120/208V-3Ph grid tied inverter with P505 optimizers. I am using USE-2 to route from the panels to the inverter. I will need to route conduit through the building to get to the inverter. My understanding is USE-2 cannot be routed indoors (even if in a raceway).
My question is can I use 600V THWN copper given the max input voltage on the inverter is 600VDC? I believe the optimizers have a maximum allowable voltage of 1000VDC. The voltage for the inverter is given as DC+ to DC- so I am assuming if this was measured between DC+ and ground it would be 300V. Thank you for any input!
My question is can I use 600V THWN copper given the max input voltage on the inverter is 600VDC? I believe the optimizers have a maximum allowable voltage of 1000VDC. The voltage for the inverter is given as DC+ to DC- so I am assuming if this was measured between DC+ and ground it would be 300V. Thank you for any input!