Conductor length restrictions from soft starters

Status
Not open for further replies.
I have 3 - 75 hp centrifugal vertical turbine pump motors to connect to new soft starters. The longest wire run is 620 ft. I am specifying 1/0 type XLPE copper in existing 2" steel. What if any restrictions might exist for such lengths from this starting method?
 
I have 3 - 75 hp centrifugal vertical turbine pump motors to connect to new soft starters. ... ... What if any restrictions might exist for such lengths from this starting method?

tim -
Have you looked at the installation manual for the starters? Perhaps it will have information.

ice
 
There are many different types of Soft Starters. You have not provided any information on which one you are using.

In terms of noise and CMV for solid state "pulsing" starters:
Ask the manufacturer. They may require you to use a special cable or an inline reactor.

In terms of failing to start for reduced voltage type starters:
Do a Transient Motor Starting analysis to determine whether or not the motors will come up to speed on Soft Start before going to full line voltage. I don't think a Soft Starter manual will tell you whether or not your motor will fail to get up to speed. Many different motors used under different loads have wildly different accelerating torque requirements and thermal limits.
Or:
1. try to start motor on worst process torque requirements from pump
2. motor starts => pat self on butt and go home
2. motor fails to start => turn up voltage, try again, don't burn up motor
 