mikehughes8

Senior Member
Location
NC
From transfomer secondary (3 phase 4 -wire) contractor has installed 90c rated 500mcm which connects to a 400A Main in the service disconnect. Article 110.14 says "Conductors with higher temperature ratings, provided the ampacity of such conductors does not exceed the 75?C (167?F) ampacity of the conductor size used" After deration the conductor meets this requirement. What I am not sure of is whether or not I am covered by Article 240.4 when applying a breaker size that is above the ampacity of the conductors. Specifically, I am having difficulty understanding exactly what is required by 240.4(B)2

500mcm @ 374A (after deration for ambient temp) and a 400A breaker
Is this allowed?
 
Specifically, I am having difficulty understanding exactly what is required by 240.4(B)2

500mcm @ 374A (after deration for ambient temp) and a 400A breaker
Is this allowed?

That is a violation, we can not roll up to the next size with transformer secondary conductors.

See 240.21(C) last sentence.

They should have used 600 Kcmil
 
From transfomer secondary (3 phase 4 -wire) contractor has installed 90c rated 500mcm which connects to a 400A Main in the service disconnect. Article 110.14 says "Conductors with higher temperature ratings, provided the ampacity of such conductors does not exceed the 75?C (167?F) ampacity of the conductor size used" After deration the conductor meets this requirement. What I am not sure of is whether or not I am covered by Article 240.4 when applying a breaker size that is above the ampacity of the conductors. Specifically, I am having difficulty understanding exactly what is required by 240.4(B)2

500mcm @ 374A (after deration for ambient temp) and a 400A breaker
Is this allowed?





If the transformer is supplied as a utility, and this is a SERVICE, your installation is fine. (I do not know if they call it a utility in Iraq, hopefully you get the gist if what I am writing)




If the transformer is not utility supplied, and is on the secondary side of a service installation, then you have the issue that Bob mentioned.
 
IMO no, but it is certainly up for debate.


Do you size a conductor for average loading or max continuous loading?

So you derate every circuit you install exposed to ambient temp based on record highs for that area?

I don't really have an opinion about it yet. I just happen to remember on a MH DVD he said it was an average but did not provide anything to explain or back up the statement.
 
So you derate every circuit you install exposed to ambient temp based on record highs for that area?

Yes, every single one and I use the highest recorded temp. :wink:

I don't really have an opinion about it yet.

It is tough to form a rock solid opinion with so little info to base it on.

I say we use the worst case temp only because that is the normal way the NEC works.

As far as I know the ampacities in 310.16 are based on conductor temp and insulation damage, few of us (outside of the utility guys) would think of sizing a conductor based on the average loading if they new that 4 hours a day for 30 times a year it would exceed the ampacity of the conductor and damage the insulation. Knowing we will exceed the temperature used for engineering the job a large number of times a year seems to me to be poor design.


That said Charlie Beck has a good argument for the other side, I believe he used the term 'insulation integrity bank' or something like that to basically say 'You can run the insulation over temp a certain number of times before damaging the insulation.' I can't say that he is wrong, I am sure we have all seen it happen in field first hand with no insulation damage.
 