mikehughes8
Senior Member
- Location
- NC
From transfomer secondary (3 phase 4 -wire) contractor has installed 90c rated 500mcm which connects to a 400A Main in the service disconnect. Article 110.14 says "Conductors with higher temperature ratings, provided the ampacity of such conductors does not exceed the 75?C (167?F) ampacity of the conductor size used" After deration the conductor meets this requirement. What I am not sure of is whether or not I am covered by Article 240.4 when applying a breaker size that is above the ampacity of the conductors. Specifically, I am having difficulty understanding exactly what is required by 240.4(B)2
500mcm @ 374A (after deration for ambient temp) and a 400A breaker
Is this allowed?
500mcm @ 374A (after deration for ambient temp) and a 400A breaker
Is this allowed?