Conductor size and why?

Status
Not open for further replies.

nickelec

Senior Member
Location
US
So I'm not that great at the theory end of things. I have been thinking about something maybe someone here can provide an explanation to. So let's say your doing a typical two family service in a residential dwelling 2 100 amp panels and meters . Now let's say we would use a #2AWG as I would . So an apprentice asked me shouldn't you use a 3/0 since you have 2 100 amp panels eaquling 200 amps and I really couldn't provide him with a proper answer. So i guess my question is y don't we add up the combined amperage . I feel like I know why but can't really put it into words.

Sent from my SM-G935P using Tapatalk
 
From my perspective, the apprentice is thinking properly as far as theory goes.

310.15(B)(7) allows #4 copper for 100A services to individual dwellings and applies to a service entrance conductor set to each of the dwellings. However, a combined service entrance conductor supplying both meters and disconnecting means cannot utilize the smaller size permitted under 310.15(B)(7) and must have a 'regular' ampacity not less than the combined calculated load. This would not necessarily require 200A service entrance conductors. It could be something less. However, assuming the total demand load approaches a 200A combined demand load total, running 3/0 copper would be correct.
 
So I'm not that great at the theory end of things. I have been thinking about something maybe someone here can provide an explanation to. So let's say your doing a typical two family service in a residential dwelling 2 100 amp panels and meters . Now let's say we would use a #2AWG as I would . So an apprentice asked me shouldn't you use a 3/0 since you have 2 100 amp panels eaquling 200 amps and I really couldn't provide him with a proper answer. So i guess my question is y don't we add up the combined amperage . I feel like I know why but can't really put it into words.

Sent from my SM-G935P using Tapatalk

You don't ever size conductors based on breakers, you size conductors based on load and adjustment factors and then you select the proper breaker.
 
You don't ever size conductors based on breakers, you size conductors based on load and adjustment factors and then you select the proper breaker.
Close but not completely true.

Code, in general, requires the OCPD be rated not less than 125% the continuous load plus 100% the noncontinuous. As a circumstance of this requirement, the circuit conductor may need be the next size larger than otherwise required.
 
Wait a second, it's the overcurrent protective device that is allowed to be the next largest size by 240.4(B) up to 800A, with the feeder meeting 125%C/100%Non-C load and adjustment and correction factors.
 
Wait a second, it's the overcurrent protective device that is allowed to be the next largest size by 240.4(B) up to 800A, with the feeder meeting 125%C/100%Non-C load and adjustment and correction factors.

That's correct. OCPD does play a role in governing the wire size, but in general, it is the load that matters first, and the OCPD calculation is a secondary criteria. So if you put a 400A breaker in an application where a 200A unit would suffice, that breaker will govern wire sizing. But if you put a 200A breaker, where your 125%/100% mix is only 180A, chances are, you only need 180A worth of wire.
 