conductor size for 1600 amp feeder

Status
Not open for further replies.
I plan on supplying a office with a 1600 amp feeder and plan on par. conduits but can't decide on wire size. It's a 480v Y, 4 wire terminated with compression lugs on each end.
Thinking of 4 - 500mcm cu thhn in 4 - 3 inch conduits. Any thoughts?
 
Re: conductor size for 1600 amp feeder

4 sets of 500?s would only be good for 1520 amps (380 X 4). You would need to use 4 sets of 600?s for this installation. See 240.4(C)
 
Status
Not open for further replies.
Top