Chrism308
Member
- Location
- Hampstead NC
I have a project where the conductors are on vented cable tray up to 700' long are sized per NEC Table 310.15(B)(20) but I was told by a couple electrical engineers the conductors can hit a terminal box between cable tray and equipment or transition sizes within the electrical equipment to change conductors to 75C ampacity per Table 310.15(B)(16) for terminations onto 2500 amp breaker. I have never used this method on cable tray runs but seems to be an option to take advantage of the 310.15(B)(20) ampacities for long cable tray runs opposed to sizing full conductor runs up to 700' long per 310.15(B)(16). Any help, NEC references, web links or photos of an installation like this would be greatly appreciated.
Thanks
Thanks