I am sizing conductors for a Freeway Lighting System in CA.
I have 25 - 310 watt lights on a 120/240 volt 1 phase 3 wire system. (lights are run on 240 volts).
My question is this: Am I allowed to downsize the conductors as the circuit gets farther away from the service point and the load (current is smaller).
I calculate about a 5% voltage drop with a #1/0 wire for part of the system. Do I have to use the #1/0 wire through the entire circuit or can I down size the conductor as the load drops farther from the service point. It would seem overkill to use say a #1/0 between the 24th and 25th lights on the circuit.
Any advise would be helpful.
I have 25 - 310 watt lights on a 120/240 volt 1 phase 3 wire system. (lights are run on 240 volts).
My question is this: Am I allowed to downsize the conductors as the circuit gets farther away from the service point and the load (current is smaller).
I calculate about a 5% voltage drop with a #1/0 wire for part of the system. Do I have to use the #1/0 wire through the entire circuit or can I down size the conductor as the load drops farther from the service point. It would seem overkill to use say a #1/0 between the 24th and 25th lights on the circuit.