Fitzdrew516
Senior Member
- Location
- Cincinnati, OH
I’m in the middle of designing a service to a new fire pump building. I have attached a PDF for reference. Does this sizing seem ok or does anyone have any issues with this set up?
Note 2 - will be sized as normal for the 60A panel.
Note 7 - will indicate wire size for 125% of the FLC of the jockey pump. (480, 3p, 1.5 HP Pump = 3A FLC (per 430.250)*1.25 = 3.75A = #12G wire)
Note 8 - will indicate wire size for 125% of the FLC of the fire pump. (480, 3p, 75HP Pump = 96A FLC (per 430.250)*1.25 = 120A = #1G wire)
Note 1 (service conductors) –Here’s where I’m not so sure. I’m assuming I would just add the 60A+120A+3.75A and then size the wire for that which would equal 183.75A or 3/0 wire. Note – voltage drop on this size is under the required 15%. This seems like the common sense way to size things, but I can’t find anything that verifies my thought process and I know fire pumps can be tricky.
If anyone could provide some insight I’d appreciate it.
Thanks,
- Drew
Note 2 - will be sized as normal for the 60A panel.
Note 7 - will indicate wire size for 125% of the FLC of the jockey pump. (480, 3p, 1.5 HP Pump = 3A FLC (per 430.250)*1.25 = 3.75A = #12G wire)
Note 8 - will indicate wire size for 125% of the FLC of the fire pump. (480, 3p, 75HP Pump = 96A FLC (per 430.250)*1.25 = 120A = #1G wire)
Note 1 (service conductors) –Here’s where I’m not so sure. I’m assuming I would just add the 60A+120A+3.75A and then size the wire for that which would equal 183.75A or 3/0 wire. Note – voltage drop on this size is under the required 15%. This seems like the common sense way to size things, but I can’t find anything that verifies my thought process and I know fire pumps can be tricky.
If anyone could provide some insight I’d appreciate it.
Thanks,
- Drew