AFAIK, the issue comes up much more often with GTI output going to a general use subpanel than for a dedicated combiner panel. In the former case, some AHJs will apply the 120% rule to the feeder as well as the subpanel bus (even though there is currently no way to connect a load to the feeder wires in the middle.)...
Not a single one of us is designing AC combiners and the conductors between them and the point of interconnection such that all the breakers fed by inverters plus the OCPD at the interconnection are less than 120% of the combiner busbar and conductor ratings. Not a single AHJ that I know of has held any of our feet to the fire to make us do this. The crux of the biscuit as I understand it is that either the inverters can feed the panel in normal operation, or the service can in the event of a fault, but not both.