So nice guy that I am, I am putting a generator in for my daughter's mom. It is a 12kW USED GENERAC. The breaker on the gennie is a 50 Amp. Looks to me for the 10 feet I need to run, #8 THHN is fine.
BUT, I thought I read that I need to use 115% of the gennie rating. This would mean I need to go to #6 THHN.
Am I misunderstanding things?
Please help as this IS a "freebie"... ( I know im too nice, at the price of wire and gas for the truck......)
Howard