If there are two loads one 40 amps the other 17 amps they may or may not operate at the same time is the 60 amp OCPD permitted on a feeder rated at 55 amps?
In your above example the load is under 55 amps.
If the load is above the rating of the conductor you can not use that conductor.
Lets say the non continuous load is 56 amps, you can use a 60 amp breaker but you would need to use 4 AWG NM or 6 AWG pipe and wire.