Donald Sherman
I've always been taught that my conductor size couldn't be smaller than what the breaker is sized for. We have an HVAC distributer who is telling my employees differant.
Example: Heat pump outdoor condensor section
min. brch. cir. ampacity 24
min. and max circuit breaker protection 40 amps. per nameplate.
They say we can install the 40 amp breaker on existing circuit that had a #10 NM-B romex wire. I was always thought you couldn't put larger than a 30 amp breaker on this wire.
Which way is correct?