Section 430.22 states that the minimum conductor size for leads are to be at 125% of FLA. While the protective device is set to 125% of the FLA per 430.32, if this protective device is adjustable, and has a range that is higher than the "125% rated" conductors, what do you size the conductors too?
To relate some more material from the NEC -
Section 240.4 (B) and 240.6 (B) & (C), indicate its ok size the conductors to the "adjusted" setting of the overcurrent device. It also seems to correlate that you can use the next standard size up overcurrent device.
In this case, do you have to size your conductors up for motor applications?
To relate some more material from the NEC -
Section 240.4 (B) and 240.6 (B) & (C), indicate its ok size the conductors to the "adjusted" setting of the overcurrent device. It also seems to correlate that you can use the next standard size up overcurrent device.
In this case, do you have to size your conductors up for motor applications?