ohmboyz
Member
- Location
- Millbrae CA, San Mateo
Hi all
This is my first post. I have a question about conductor sizing and double derating. Here are the conditions: branch circuit of 30 amp continuous load, thhn copper, 4 wires in a raceway and a terminal temp rating of 75 degrees C. After applying 210.19 for the continuous load, and using the 75 degree column in table 310.15 (B) (16), a number 8 wire is chosen.
Now, if I understand correctly that I do not have to double derate, then when I do my adjustments for conduit fill, I can use the listed load of 30 amps (not 37.5 ie- 30 X 125%) and multiply by 80%.
Is that correct?
This is my first post. I have a question about conductor sizing and double derating. Here are the conditions: branch circuit of 30 amp continuous load, thhn copper, 4 wires in a raceway and a terminal temp rating of 75 degrees C. After applying 210.19 for the continuous load, and using the 75 degree column in table 310.15 (B) (16), a number 8 wire is chosen.