Conductor ampacity is conductor ampacity. That's what the OCPD must protect.
That is my question: what is ampacity? Is this a correct statement:
Ampacity is either, 1) the value given in 310.15(B)(16) under the column that the insulation is rated at (or required to be rated at by another code article) if there is no derating from conditions of use, or 2) the value given in 310.15(B)(16) under the column that the insulation is rated at multiplied by the applicable derating factors. (assume 310.15(B)(16) is the applicable chart for the installation)
In other words, ampacity is the number from the appropriate chart (i.e. 310.15(B)(16) adjusted for derating factor/conditions of use (if applicable). Correct? Maybe sounds like a stupid question, this thread just really confused me.
The ampere values you use for terminal temperature limitations are only for the purpose of establishing the minimum conductor SIZE... which has nothing to do with AMPACITY.
Three parts to conductor determination:
- Minimum SIZE
- Minimum AMPACITY
- Maximum-permitted PROTECTION
Only the latter two are interdependent.
Got it, makes sense.
I really appreciate the help guys...really... but....Can I get an answer to my question? I word a question in a way that makes sense to me and answering the question directly rather than rewording it, adding additional information, and never really answering it, is the easiest way for me to make sure I have it straight:
What is the maximum size breaker (for Smarts example)? Is it the lesser of:
1) the number resulting after applying the adjustment factors to the 90 degree column ampacity
2) the 75 degree column ampacity (termination limitation) ?
(Ignore any NEC or manufacturer equipment protection requirements, and next size up rule)