I have 2 sets of 600 kcmil service conductor into 480/277 three phase 800A main service panelboard P at Bldg A. The panelboard has 200A feeder breaker with 3/0 AWG phase conductors feeding separate Bldg B. NEC 2014 section 250.32 requires grounding electrode system at Bldg B.
My service entrance conductors are 2 sets of 600 kcmil and my feeder conductors are 3/0 AWG. Grounding electrode conductor are sized based on service entrance conductor but for Bldg B it’s confusing.
Question the grounding electrode conductors size at Bldg B should be based on 3/0 AWG or based on 2 sets of 600kcmil?
Sent from my iPhone using Tapatalk
My service entrance conductors are 2 sets of 600 kcmil and my feeder conductors are 3/0 AWG. Grounding electrode conductor are sized based on service entrance conductor but for Bldg B it’s confusing.
Question the grounding electrode conductors size at Bldg B should be based on 3/0 AWG or based on 2 sets of 600kcmil?