Devin Hanes
Member
- Location
- United States
That was my interpretation as well.
Anyone want to take a stab at explaining Note 2?
Here's my stab, based on my bias of what I thought the Code allowed. Like I said before though, I don't think it is clear either.
Note 2. Where there are no service-entrance conductors, the grounding electrode conductor size shall be determined by the equivalent size of the largest service-entrance conductor required for the load to be served.
"Where"=Physical Location-"the service", "the separate structure", "or at a separately derived system"
Based on 250.66
250.66 Size of Alternating-Current Grounding Electrode
Conductor. The size of the grounding electrode conductor at
the service, at each building or structure where supplied by a
feeder(s) or branch circuit(s), or at a separately derived system
of a grounded or ungrounded ac system shall not be less than
given in Table 250.66, except as permitted in 250.66(A)
through (C).
now for the "largest" issue
Note 2. Where there are no service-entrance conductors, the grounding electrode conductor size shall be determined by the equivalent size of the largest service-entrance conductor required for the load to be served.
This is the exact language used in the tables column heading
2017

What do you think?
Last edited: