resistance said:
Ok, I'm going to open up a can of snakes---
Nice try. It is a good application of the second sentence of 110.14(C). Now go back and read the first sentence of that paragraph.
 
And while I am on this topic:
resistance said:
Mike Holt says: In general, 90 degree rated conductor ampacities cannot be used for sizing circuit conductors. However, higher insulation temperature ratings offer the opportunity of having a greater conductor ampacity for adjustment and correction purposes.
I am certain that by "a greater conductor ampacity," Mike did not mean "greater than the 75C column." Rather, I suspect that he meant "greater than you would have gotten, if you started the derating from the values in the 75C column."
 