joeyww12000
Senior Member
- Location
- Chatsworth GA
What exactly does the conductor temp rating mean from table 310.16? Lets say I had a conduit that had only one 277v, 2 wire circuit, pulled in #12 THHN. I would have no reason to derate. Normally I would use an ocpd rated for 20a or less. If I had enough CCCs to have to derate I would use the 90c column which would tell me the ampacity of #12 THHN is 30a before derating. I guess Im confused on why Im using this column all of a sudden to size my ocpd, when without derating I dont even look at this table?