Conductor transition to lower Voltage Drop

Status
Not open for further replies.

stuartdmc

Senior Member
The missing equation is the VD at the meter section. I have to start at the 4000-amp mains, from the main we run 100ft to the meter sections, In stead of starting at 0% VD, we're starting at 1.2 to 1.8% VD as worst, that means we only have 2.4% to go 600ft. to the panel, then after we reach the panel, I must allow at least 1% for the branch circuits worst case. and I don't think 1% is even good enough, the worst case branch circuit is the run to the RTU, and that can be as faraway as 100ft. plus feet.
 

oldsparky52

Senior Member
Using the full panel/feeder rating for the current is probably not even necessary. FYI I get 4% with your parameters. OP beware of some online calculators like the southwire one, they use 90% PF (which is very likely un-necessary as large resi loads will usually be resistive). That one gives 5% with the above parameters.
Dang, caught me using the 1st on line VD calculator w/out checking. Using the VD formula MH has and then using VD=IR, I come up with a VD of 7.42 volts which is about 3.6%.

I agree with your comment about the load. Thanks for the catch.
 

oldsparky52

Senior Member
The missing equation is the VD at the meter section. I have to start at the 4000-amp mains, from the main we run 100ft to the meter sections, In stead of starting at 0% VD, we're starting at 1.2 to 1.8% VD as worst, that means we only have 2.4% to go 600ft. to the panel, then after we reach the panel, I must allow at least 1% for the branch circuits worst case. and I don't think 1% is even good enough, the worst case branch circuit is the run to the RTU, and that can be as faraway as 100ft. plus feet.
Sounds like a mess.
 