stuartdmc
Senior Member
- Location
- Newport Beach, Irvine, CA
The missing equation is the VD at the meter section. I have to start at the 4000-amp mains, from the main we run 100ft to the meter sections, In stead of starting at 0% VD, we're starting at 1.2 to 1.8% VD as worst, that means we only have 2.4% to go 600ft. to the panel, then after we reach the panel, I must allow at least 1% for the branch circuits worst case. and I don't think 1% is even good enough, the worst case branch circuit is the run to the RTU, and that can be as faraway as 100ft. plus feet.