coulter said:
David -
You sound dangerously close to agreeeing with me.
Now lets take a look at what the NEC says if the customer owns the transformer, the service point is on the xfm primary. Consider an outside xfm, a ground mat under the entire area, and let's use MC-HL cable for the secondary feeders to the OCPD, 500" away. Exactly the same installation as if the utility owned the xfm, except this one is an SDS. I say we make the N-G bond either at he xfm or at the frist disconnect, but not both. 250.30.A.1.
Kind of interesting the rules change depending on who owns the xfm.
carl
We are dangerously close but I think the point of disagreement isn't the bonding requirements or the paralleling conductor requirements. . I think we are viewing SDS differently.
In your paragraph above you state that "the service point is on the xfm primary". . I don't believe the service
point matters in determining an SDS. . The service point matters in determining NEC jurisdiction but not SDS.
Service Point. The point of connection between the facilities of the serving utility and the premises wiring.
Separately Derived System. A premises wiring system whose power is derived from a source of electrical energy or equipment other than a service.
[ note that it says
service not
service point ]
Service. The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served.
No matter who owns the transformer or where the service point is, the question is where is the service main disconnect ? . Is it on the load side of the transformer or on the line side ? . If it's on the line side, then you have an SDS coming out of the secondary of that transformer.
If you have a transformer on the
load side of the service
point, then you have NEC jurisdiction and 250.24(A)(2) applies.
If you have a transformer on the
line side of the service
point, then you have
no NEC jurisdiction and 250.24(A)(2)
doesn't apply.
If the service
main disconnect is on the
line / primary side of the transformer, then you have a SDS and 250.30(A)(1) applies.
If the service
main disconnect is on the
load / secondary side of the transformer, then you
don't have a SDS and 250.30(A)(1)
doesn't apply.
But even if 250.30(A)(1) applies, when you're dealing with a transformer outside of the building, you're dealing with a separate structure because the transformer is "built or constructed" [ 100 defs ] in a factory. . So you have the option of connecting the 2 structures according to 250.32(B)(1) or 250.32(B)(2). . If you use (1), you have to let the neutral "float" unconnected from the ground
ing on one end or the other or you'll get a 310.4 violation. . If you use (2), you have to bond neutral to ground
ing at both ends.
David