It is important that you follow the requirements of 300.20(B).Exception: Conductors installed in nonmetallic raceways run underground shall be permitted to be arranged as isolated phase installations. The raceways shall be installed in close proximity, and the conductors shall comply with the provisions of 300.20(B).
The only application I have found this good for is for the service conductors from a padmount transformer and the switch gear inside.Originally posted by marissa2:
but if is allowed only in limited applications why would you want too.