Hello Everyone,
I have one question:
Can we install conductors coming out of two separate service equipment enclosures in the same conduit ?
I am not sure that the NEC Article 300.3 below allows it.
300.3 Conductors.
(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
Thanks,
Peter Phi
I have one question:
Can we install conductors coming out of two separate service equipment enclosures in the same conduit ?
I am not sure that the NEC Article 300.3 below allows it.
300.3 Conductors.
(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.