So I've gotten into a situation where I need to supply power to a fire pump. The issue is that the main electrical service is going to be in a "penthouse" at roof level. So I need to do a line side tap pull section and then have a separate disconnect for the fire pump, i know that, but the question is about the conductor run.
I know that the conductors need to either be protected in a number of ways, or be "outside the building". So I guess the question is: Is running the conductors across the roof and down the wall out to the pumphouse located by the fire pond OK? Would these conductors be considered "outside the building". I think by code standards they are technically considered "outside the building", but in all practicality is the inspector going to look at conductors on the roof and have an issue, because let's be honest... we're supposed to be protecting the feeders to the fire pump to ensure the fire pump functions properly- What if the fire burns through the conductors on the roof?
Any thoughts/suggestions/discussion would be helpful.
Thanks,
Drew
If the service entrance equipment is on the roof, I would guess that the POCO meter is somewhere at or near ground level ... that would imply that there is a CT cabinet adjacent to the meter from which the fire pump feeder could be tapped and routed to the remote pump building.
The fire pump controller is a service disconnect and is not included in the maximum 6 disconnect count and not subject to the grouping of disconnects rule, so unprotected service conductors from the downstream side of the meter to the fire pump controller / pump are permitted.
There will also need to be branch circuits (or a separate feeder to a general purpose panel in the pump building) from the building power distribution equipment to power any lights, receptacles, heating equipment and jockey pump that may be located in the fire pump building - that equipment cannot be served from the fire pump feeder as I read the code.
Technically, routing the fire pump feeders across the roof and down the exterior surface of the wall is "physically routed outside a building" (NEC 695.6(A)(1)), although it does seem like running those feeders across the roof exposes them to damage or failure due to a fire inside the building that the pump is trying to protect.
On at least one past project that I have been involved with, a fire pump showed up after the service was installed and after the floor slab was poured. This pump was inside the building and tearing up the floor was a very costly option. In the end, a conduit was laid directly on top of the floor slab at the bottom of the wall and encased in concrete that was 2 inches above the top of the conduit and that extended 2 inches past each side of the conduit - in compliance with 695.6(A)(2)(d)(1). Sort of like your situation of running it across the roof of the "on fire" building, but still code compliant.