can panel feeder conductors be mix as in copper and aluminum if proper sizing is used for the load or can the ground wire be aluminum if the feeder wires are copper
Is it time to share?dana1028 said:I have some nice close up photos of the arrangement but never have bothered to learn how to post them here.
That is a violation of 310.4(B). :roll:dana1028 said:. . . and phase A was one of each. . .
That's an issue. Paralleled conductors are supposed to have the same characteristics, including insulation type.dana1028 said:. . . phase A was one of each.
Each phase's paralleled conductors must be identical to assure equal current distribution. One phase's characteristics need not match that of another phase, though.76nemo said:It's hard to believe this is allowed, especially comparing one phase to the next. I have never seen a mismatch like that.
Can you please fill me in some more?????????
I am totally dumbfounded!
310.4(C) Separate Cables or Raceways. Where run in separate cables or raceways, the cables or raceways with conductors shall have the same number of conductors and shall have the same electrical characteristics. Conductors of one phase, polarity, neutral, grounded circuit conductor, or equipment grounding conductor shall not be required to have the same physical characteristics as those of another phase, polarity, neutral, grounded circuit conductor, or equipment grounding conductor to achieve balance. :smile:76nemo said:. . . Can you please fill me in some more? . . .