thanks for your answer,so in theory if a service panel or a piece of equipment is installed and fed with conduit then the equipment grounding conductor chart is not needed.You can certainly put in a proposal to require a wire type EGC in a metal raceway, your proposal (or PI) would be for the 2026 NEC, plenty of time to gather documentation. Past proposals to require wire type EGC have been rejected with the comment that properly installed RMC, EMT, IMC is an acceptable EGC, Keep in mind who is on the CMP, take a look at CMP No. 8.